Re: 32 Old Slip AC Outage and 60 Hudson Verizon failure
From: "Vincent J. Bono" <vbono () vinny org>
Date: Wed, 12 Sep 2001 09:28:24 -0400


Status:

We are at 32 Old Slip on the 4th floor.  AC power is down and our generator
air intake is clogged and the sensors shut it down.  Batteries are fine (we
have 27 hours left) but the HVAC is on generator only.  Since we are south
of 14th street we are awaiting permission to enter the area to effect
repairs.  Luckily our staff members who were outside during the collapse are
fine which was our main concern.

Sincerely,
GLOBAL NAPS, INC.

Vincent J. Bono
Vice President
Engineering


----- Original Message -----
From: "Robert Boyle" <robert () tellurian com>
To: <nanog () merit edu>
Cc: <engineering () tellurian net>
Sent: Tuesday, September 11, 2001 10:36 PM
Subject: 32 Old Slip AC Outage and 60 Hudson Verizon failure



Our equipment at 32 Old Slip is not operational. This is apparently
due to AC power failure and an inability to start the generators due
to ash in the air (this may be a choice as well). Anyone running at
32 Old Slip (TCG/Eagle/Focal/GNAPs are the four I know of on the
fourth floor) on DC power is on battery or offline.

Our POP at 60 Hudson is up with the MFS/WorldCom provided backhaul
circuit to our 34 Exchnage Place Jersey City location, but all
Verizon circuits terminating at 60 Hudson are down/down. All MFS/WCom
circuits seem to be ok so far...

-Robert