nanog mailing list archives
Re: FDDI concentrator w/DC power
From: feldman () MFSDatanet COM (Steve Feldman)
Date: Thu, 19 Sep 1996 11:18:08 -0700
I cannot find a FDDI concentrator that runs on -48 VDC. Is there a product I've missed? This shortage of DC-powered concentrators might explain some of the transient outages during power problems at MAE-East, perhaps?
The FDDI concentrators at MAE East (along with all the other AC-powered
infrastructure equipment) are powered by a UPS with at least 5 hours of
battery power. In addition, all customer equipment co-located at the
1919 Gallows P-1 MAE facility is powered by the UPS.
Here's a note from the facilities manager for MAE East on the subject of
power:
---------------------
MAE East at 1919 Gallows Road P-1 level is configured as follows:
- four (4) two hundred amp Lorain rectifiers.
- three (3) 1600 amp battery stacks.
- one (1) 30 KVA UPS system.
- generator umbilical is installed for use with MFS owned 150 KW
mobile generator when required. Generator can be on site within
one hour and has sufficient fuel to run for 24 hours.
All racks installed at MAE East are equipped with a multi outlet power
strip with a dedicated 20 amp AC circuit to the UPS system. Therefore
all customer electronics and all MFS equipment requiring AC power are
provided with filtered AC power via the UPS and have a five hour
battery reserve. In addition, all racks have a minimum of 15 amps DC
power to a Hendry fuse panel. This panel is served via the DC power
plant which provides a minimum of eight hours of battery reserve.
The standard MFS offering does not include UPS power in the MAE
facilities. At MAE East we have gone one better and provided all
customers with UPS. This is a premium service provided at no
additional cost.
As a final note, we are about to begin construction to upgrade
facilities at both 8100 Boone Blvd. and MAE East. This work will
include the installation of a permanent 900 KW generator.
---------------------
Steve
- - - - - - - - - - - - - - - - -
Current thread:
- FDDI concentrator w/DC power Matthew Kaufman (Sep 19)
- <Possible follow-ups>
- Re: FDDI concentrator w/DC power Steve Feldman (Sep 19)
- Re: FDDI concentrator w/DC power Nathan Stratton (Sep 23)
