At 2:03 PM -0400 10/19/02, Sean Donelan wrote:
Stuff happens to everyone, its how you respond. Would your company have been able to recover as quickly? http://media.corporate-ir.net/media_files/nsd/tess/consumermail.html Thanks to folks for pointing this one out.
Good job.I've had to deal with assorted water problems, thankfully not recently. Some lessons were learned. These water problems were indirectly or directly caused by firefighting.
1. When the data/comm center is on a bottom floor, consider floor drains at
the time of installation. Might want emergency access to pumps, or even
wet-dry shop vacs.
2. We had a repeated problem in several moderate-rise buildings where there
were fairly frequent, although small, fires on upper floors. Water, of
course, runs downhill. Some things done (this was the US Senate offsite
computer center)
a. Put waterproof gaskets on the emergency stairs that had entrances
from the control room.
b. When it happened often enough, we mounted rolled-up plastic tarps on
rollers suspended from the ceiling, with a good solid handle dangling
down on a rope. During the peak problem period, we'd hear an alarm,
pull the tarps over the equipment, and then do a fast power-down (not
necessarily emergency pull--this depended on heat buildup). The tarps
were a few inches over the top of the racks, to leave some room for
emergency airflow during cooldown.
3. Consider putting data centers not in the ground floor on the basement,
but not too high either. Sean, I believe, knows the specific NFPA rule,
but IIRC you can't have a UPS with acid electrolyte above the third floor.
So, you can put a data center on the 2nd floor and both allow the UPS
and have a place for the water to drain.
Current thread:
- The power of water Sean Donelan (Oct 19)
- Re: The power of water Howard C. Berkowitz (Oct 20)
- Re: The power of water Pete Ehlke (Oct 20)
- Re: The power of water John Kristoff (Oct 23)
- <Possible follow-ups>
- Re: The power of water Crist J. Clark (Oct 21)
- Re: The power of water David Lesher (Oct 21)
- Re: The power of water Howard C. Berkowitz (Oct 20)