On Dec 2, 2010, at 8:46 AM, Leo Bicknell wrote:
In a message written on Thu, Dec 02, 2010 at 11:32:16AM -0500, Jay Ashworth wrote:No, I'm pretty sure he means "across the 2 high legs of a 120/208 3ph Wye service", and I'd never heard that idea suggested before. I can see why it reduces the amount of copper you need to run, but it seems as if it would have compensating disadvantages, though I can't think precisely what they might be at the moment.In most residential / small business construction in the US you will find "240V single phase with neutral". There are two hot wires and a neutral from the provider. Hot to hot is 240, hot to neutral is 120. Most colos run their back end plant (e.g. UPS's, Gensets, etc) on 480v 3-phase power. The typical way they get 120v power is to transform that to a 3-phase Y wired output, also known as 3-phase 4 wire. Each hot leg is 120v to the neutral (the fourth wire). You can run hot to hot here as well, where the voltage is 208v. The trick with 208v loads in this situation is you want to keep the load across each pair of phases roughly balanced. What can be particularly confusiong here is the panels look exactly the same. The same physical panel layout your house gets with 2 phases in plus a neutral is now two of the three phases from the three phase power go in, plus a neutral. Same breakers are used, with hot to hot being 208 volt. The difference is, in the colo there are three of them: A N B B N C C N A | | | | | | | | | Panel 1 Panel 2 Panel 3 With A, B, and C being the 3 phases, and N being the neutral.
It is not uncommon for three-phase panels to be different and have all three phases in the panel each phase feeding every third breaker slot. Owen
Current thread:
- Want to move to all 208V for server racks Jay Nakamura (Dec 02)
- Re: Want to move to all 208V for server racks William Herrin (Dec 02)
- Re: Want to move to all 208V for server racks Ingo Flaschberger (Dec 02)
- Re: Want to move to all 208V for server racks Jay Nakamura (Dec 02)
- Re: Want to move to all 208V for server racks Seth Mattinen (Dec 02)
- Re: Want to move to all 208V for server racks Ingo Flaschberger (Dec 02)
- RE: Want to move to all 208V for server racks Alex Rubenstein (Dec 02)
- Re: Want to move to all 208V for server racks Jay Ashworth (Dec 02)
- Re: Want to move to all 208V for server racks Leo Bicknell (Dec 02)
- Re: Want to move to all 208V for server racks Owen DeLong (Dec 02)
- Re: Want to move to all 208V for server racks Kevin Day (Dec 02)
- Re: Want to move to all 208V for server racks Jay Ashworth (Dec 02)
- Re: Want to move to all 208V for server racks Ingo Flaschberger (Dec 02)
- Re: Want to move to all 208V for server racks Ingo Flaschberger (Dec 02)
- Re: Want to move to all 208V for server racks Kevin Day (Dec 02)
- Re: Want to move to all 208V for server racks Ingo Flaschberger (Dec 02)
- Re: Want to move to all 208V for server racks Kevin Day (Dec 02)
- Re: Want to move to all 208V for server racks Ingo Flaschberger (Dec 02)
- Re: Want to move to all 208V for server racks Jay Ashworth (Dec 02)
- Re: Want to move to all 208V for server racks Steven Bellovin (Dec 02)
- Re: Want to move to all 208V for server racks Jay Nakamura (Dec 02)