nanog mailing list archives
Re: L6-20P -> L6-30R
From: William Herrin <bill () herrin us>
Date: Wed, 19 Mar 2014 12:24:38 -0400
On Wed, Mar 19, 2014 at 11:22 AM, Lamar Owen <lowen () pari edu> wrote:
Just replacing an L6-20P with an L6-30P on a 20A-listed PDU would be unsafe and (IMO) unwise, since the breaker in the input of the PDU does not protect the flexible cord's conductors from internal overcurrent faults.
Yet an 18 awg PC power cable is perfectly safe when plugged in to a 5-20R on a circuit with a 20 amp breaker. Get real man. You got two things right: The NEC (and related fire codes) don't apply to supply cords of appliances in circumstances such as OP's PDU. The modification cancels the UL certification. If you have an external requirement to use only UL certified components then you can't make any modifications no matter how obviously safe they are. By the way, you either don't have that requirement or you're breaking it. Your custom network cables are not UL certified. Regards, Bill Herrin -- William D. Herrin ................ herrin () dirtside com bill () herrin us 3005 Crane Dr. ...................... Web: <http://bill.herrin.us/> Falls Church, VA 22042-3004
Current thread:
- RE: L6-20P -> L6-30R, (continued)
- RE: L6-20P -> L6-30R Alex Rubenstein (Mar 18)
- Re: L6-20P -> L6-30R Rob Seastrom (Mar 19)
- RE: L6-20P -> L6-30R Alex Rubenstein (Mar 19)
- Re: L6-20P -> L6-30R Rob Seastrom (Mar 19)
- Message not available
- Re: L6-20P -> L6-30R Larry Sheldon (Mar 19)
- Re: L6-20P -> L6-30R William Herrin (Mar 18)
- Re: L6-20P -> L6-30R Wayne E Bouchard (Mar 18)
- Re: L6-20P -> L6-30R Lamar Owen (Mar 19)
- Re: L6-20P -> L6-30R William Herrin (Mar 19)
- Re: L6-20P -> L6-30R Lamar Owen (Mar 19)
- Re: L6-20P -> L6-30R William Herrin (Mar 19)
- Re: L6-20P -> L6-30R Chuck Anderson (Mar 19)
- Re: L6-20P -> L6-30R William Herrin (Mar 19)
- Re: L6-20P -> L6-30R Jay Ashworth (Mar 19)
- Re: L6-20P -> L6-30R Aaron (Mar 19)
- RE: L6-20P -> L6-30R Alex Rubenstein (Mar 19)
- Re: L6-20P -> L6-30R Jay Ashworth (Mar 19)
- Re: L6-20P -> L6-30R William Herrin (Mar 19)
- Re: L6-20P -> L6-30R Jay Ashworth (Mar 19)
- Re: L6-20P -> L6-30R William Herrin (Mar 19)
- Re: L6-20P -> L6-30R Chuck Anderson (Mar 19)
