nanog mailing list archives
Re: L6-20P -> L6-30R
From: Lamar Owen <lowen () pari edu>
Date: Wed, 19 Mar 2014 14:27:38 -0400
On 03/19/2014 02:05 PM, William Herrin wrote:
50 watts DC. It won't electrocute you (that's AC) but it's the same power that makes a 40 watt bulb burning hot.802.3af is limited to 15.4W, and 802.3at to 25.5W. The limits for Class 2 and 3 circuits are found in Chapter 9, Table 11 (A and B), of the NEC (Table 11(B) for DC circuits, and for a power source of 30 to 60 volts a Class 2 circuit can have, for a 44VDC supply power, up to 3.4A available (a max nameplate rating of 100VA). For AC, Table 11(A) tells me that a 120VAC circuit, to meet Class 2, must be current-limited to 5mA.
BICSI has a good set of slides on the NEC at http://www.bicsi.org/uploadedfiles/Conference_Websites/Winter_Conference/2012/presentations/Interpreting%20the%20National%20Electrical%20Code.pdf
Current thread:
- Re: L6-20P -> L6-30R, (continued)
- Re: L6-20P -> L6-30R William Herrin (Mar 19)
- Re: L6-20P -> L6-30R Jay Ashworth (Mar 19)
- Re: L6-20P -> L6-30R Aaron (Mar 19)
- RE: L6-20P -> L6-30R Alex Rubenstein (Mar 19)
- Re: L6-20P -> L6-30R Jay Ashworth (Mar 19)
- Re: L6-20P -> L6-30R William Herrin (Mar 19)
- Re: L6-20P -> L6-30R Jay Ashworth (Mar 19)
- Re: L6-20P -> L6-30R William Herrin (Mar 19)
- Re: L6-20P -> L6-30R Chuck Anderson (Mar 19)
- Re: L6-20P -> L6-30R William Herrin (Mar 19)
- Re: L6-20P -> L6-30R Lamar Owen (Mar 19)
- Re: L6-20P -> L6-30R Lamar Owen (Mar 19)
- Re: L6-20P -> L6-30R George Herbert (Mar 18)
- Re: L6-20P -> L6-30R Jay Hennigan (Mar 20)
- Re: L6-20P -> L6-30R Owen DeLong (Mar 20)
- Re: L6-20P -> L6-30R Chuck Anderson (Mar 19)